Agreed, but it would be good to measure my current airflow. That info would help me estimate how many more CFM are needed.
How do you determine where to place the marks on the card stock? How do you translate those marks into feet/minute?
I tested the effect of the warm exhaust from the tent on the “outside” temperature reported by the digital controller, which is attached to the tent. I started with everything but the ceiling fan off. Then, I turned the lights, exhaust fan, and circulating fan on full and let the temps stabilize. Results:
Starting: 74° inside tent; 75° outside.
Ending: 100° inside; 83° outside.
So the warm exhaust increased the room temp at the controller by 8°, which implies that piping the exhaust out a window would reduce both temperatures by the same amount. Comparison with my previous test, which ended with 100° inside and 84 - 86° at the controller, shows the ceiling fan had little, if any, effect on the temp at the controller or in the tent once the lights were turned on. We know already that I should lower the lights and dim them – that will reduce both temperatures. But now I know the reduction I could get by piping the exhaust outdoors.
I also tested the effect of the exhaust fan’s speed:
| Inside | Outside | |
|---|---|---|
| Initial temps | 77° | 78° |
| Fan speed 7 | 101 | 83 |
| Fan speed 5 | 104 | 83 |
| Fan speed 3 | 109 | 84 |
| Fan speed 7 | 101 | 83 |
| Fan speed 10 | 99 | 83 |
| Fan speed 7 | 100 | 83 |
The fan speed had little, if any, effect on the outside readings. Increasing speed reduced the inside temp consistently throughout the range of speeds tested, but with diminishing returns: Speeds 3 & 5 differ by 5°, speeds 5 & 7 differ by 3°, and speeds 7 & 10 differ by only 1 or 2°. I suspect this nonlinearity is due to the filter. That is, the effect of its constriction is not a constant – it increases as the fan approaches the filter’s rated CFM.
In any case, the results suggest that @PhotoFinisH is correct: Increasing my system CFM would cool the tent further.