Public Service Announcement- Electrical Fire

Be sure to verify your current draw, wire size and circuits & breakers when setting up a grow room :skull_and_crossbones:

Yesterday I tried to burn down the house. Only been in this house for less than a year. Two 20A garage circuits listed in my breaker box. Like a fool, I never verified.

Come to find out yesterday after an arc and melting of the common wire on the circuit that the garage was in fact only one circuit. And, the circuit was wired with OLD style Romex wire. It was 12/2 but OLD. And I had the tent running, lights, additional lights, a refrigerator, and the AC unit running. Apparently all in one circuit. Breaker never tripped, just blow off the common wire. Near disaster.

I ran two new 20A circuits last night.

This all happens while at work and only noticed something was wrong because I couldn’t connect to my app. My son was able to get there after an hour to verify something was really wrong. I got lucky this time……

I’m back up and running after being down for a few hours.

7 Likes

I should mention that it was running fine for the last several weeks….

5 Likes

Glad everything turned out, it is important to know how much electric draw you’re placing on your panel with your grow.

4 Likes

Yeah, my mistake was assuming they were two different circuits. Come to find out that many of the labels on the circuit breaker don’t match.

Someone hacked the wiring over the years…

2 Likes

One thing I’ve learned from maintenance, the breakers are usually labeled incorrectly, or not labeled.

4 Likes

We did some kitchen renovations years ago, I went through and labeled everything in the box and hung a color coded printout in a clear pocket on the door of the breaker box. I was out of town a lot and the wife and kids were home, I needed them to not be guessing if there was an issue.

I ran two 20amp 115v circuits and one 20amp 220v circuit (light) just for my lung room.

3 Likes

@VBGrower Glad you still have a house, could of been bad, and you have that right if you are running indoors MAKE sure your circuits are correct, I was lucky enough to be in mid stride of redoing the basement and found a 220 line for old kitchen range and ovens, put in a new sub panel and split so there is plenty of room to run 2 tents safely.
Bestest advice you can give right there!! :+1: :beers:

2 Likes

Damn brother I’m glad everything’s okay. My son and I wired our grow room so almost everything had its own circuit. It’s really important not to overload and know what you’re plugging in. It’s rare that somebody gets lucky like you did when the breaker doesn’t trip.

We have a little convenience store up on the corner the guy got a new slushy machine plugged it into the outlet and burnt the entire store down. Took over a year to rebuild it.

3 Likes

@Lostgirl - ugh!

Yeah, yesterday afternoon was a :poop: show at my place…

While going through the breaker panel I found a few other loose connections so I’ll take that as a win. Plus, two new dedicated circuits…. Thinking about adding another for the fun of it……

3 Likes

My dehumidifier has its own circuit. Both air conditions have their own circuits. The light has its own circuit.

Then the few fans that I have or small enough for the regular room wall outlets. It’s definitely dangerous :poop:

And if you don’t know what you’re doing it can be very expensive. Glad it all worked out for you buddy

3 Likes

First, and I shoulda said this earlier, really glad it didn’t go worse for ya. Truly!!

Yeah, my old house is like 65 / 70 years old. the wiring I found… :scream: :fearful: :scream:

They had 2 conductor fiber / paper sheathed wire spliced together with no wire nuts or anything other than twisted together and electrical tape. WTF!

Better that you found it now and take care of it before it goes bad bad. :four_leaf_clover: :four_leaf_clover: :love_you_gesture:t4: :love_you_gesture:t4:

1 Like

The real question should be…is the breaker bad? Like exceeding the rating and did not trip or was it a loose wire. Generally speaking, #1 cause of electrical fure is a poor termination. I would want to know which. You should always know how much power u are putting on a circuit. Should never exceed 80% of breaker rating, in fact its code unless its listed at 100% load which in a residential world, i have never seen. In essence, u should never load a 15a breaker to more then 12a, never exceed 16a on a 20 amp breaker. So at 1920 watts for a 20 amp breaker. (Current x voltage=power) to exceed that in a basic grow setup is kinda crazy. 20 yr journeyman electrician local 86. Any questions…feel free.

One more thing, federal pacific breakers from the 60’s and 70’s were known to fail. In fact i have them as well. Lol im the guy who never upgraded his own service bc i do it all day long. But i also verified all loads with a amp meter to be certain im ok. My point is to be aware of federal pacific breakers.